Author Topic: Viessmann Boiler pcb failure  (Read 3234 times)

0 Members and 1 Guest are viewing this topic.

Shackeng

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Ramsbury
  • Posts: 7762
    • 3.2 Elite 2.0 TitX Mondeo
    • View Profile
Viessmann Boiler pcb failure
« on: 19 March 2018, 20:00:33 »

Typical, boiler failed to start yesterday AM, on of the coldest days of the year! Unfortunately no fault codes, just no flame indicator. Last fault code from a previous temporary failure a while ago suggested a faulty ignition electrode, so changed that today with no luck. Very helpful guy at Viessmann talked me through the trouble shooting - the manual is 'somewhat tricky' to follow - to deduce it is the pcb, (at £360 and change) >:( However it is 9 years old, and he said that changing both electrodes was sensible at that age anyway. Bloody annoying as it is almost certainly one small twopenny item that's failed on the board, which is impossible for me to test. New board arrives tomorrow on overnight delivery.
Mrs S not pleased at having to rely on fan heaters and a gas fire.
Logged

STEMO

  • Guest
Re: Viessmann Boiler pcb failure
« Reply #1 on: 19 March 2018, 20:10:44 »

If it's nine years old, Chris, you really should be thinking about replacing it. It will probably go on Christmas Day next time.
With this being OOF and all, most people will say I'm talking shite, and that their 37 year old boiler is fine..........don't listen.
Logged

Viral_Jim

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Telford
  • Posts: 4246
    • Too many, mostly broken
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #2 on: 19 March 2018, 20:44:08 »

If it's nine years old, Chris, you really should be thinking about replacing it. It will probably go on Christmas Day next time.
With this being OOF and all, most people will say I'm talking shite, and that their 37 year old boiler is fine..........don't listen.

You jest, but when we moved into our place, the boiler was exactly two months younger than me. Chewed through £120 gas each month and the only room you didn't have to wear a jumper in was the bloody boiler room. The new one was about a £3k install and now gets through around £55 pcm. Payback is around 4yrs, oh and that doesn't include wear 'n' tear on my sweaters  ::)  ;D

It's also been faultless (touch wood) and is only half way through its 8yr warranty  :o.

But yes STEMO, as you say, I'm sure the old one was much better, in oh so many ways...
Logged

Marks DTM Calib

  • Administrator
  • *****
  • Offline Offline
  • Gender: Male
  • West Bridgford
  • Posts: 33813
  • Git!
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #3 on: 20 March 2018, 08:09:04 »

Typical, boiler failed to start yesterday AM, on of the coldest days of the year! Unfortunately no fault codes, just no flame indicator. Last fault code from a previous temporary failure a while ago suggested a faulty ignition electrode, so changed that today with no luck. Very helpful guy at Viessmann talked me through the trouble shooting - the manual is 'somewhat tricky' to follow - to deduce it is the pcb, (at £360 and change) >:( However it is 9 years old, and he said that changing both electrodes was sensible at that age anyway. Bloody annoying as it is almost certainly one small twopenny item that's failed on the board, which is impossible for me to test. New board arrives tomorrow on overnight delivery.
Mrs S not pleased at having to rely on fan heaters and a gas fire.

Chances are its a few dried out electrolytics
Logged

Viral_Jim

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Telford
  • Posts: 4246
    • Too many, mostly broken
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #4 on: 20 March 2018, 09:35:19 »

Shackeng, if you’re intending to keep the boiler long term, maybe worth hanging on to the old pcb, and testing m/repairing it so you have a spare you can drop in in future.
Logged

omegod

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • liverpool
  • Posts: 4344
    • 2017 Seat Ateca
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #5 on: 20 March 2018, 09:41:31 »

Chap I know makes a fortune from replacing these boards, he simply resolders the old ones joints and supplies/fits them as cheap replacements as he has a massive stash of spares
Logged
Happy to do Omega servicing etc around Merseyside,cruise activation, airbag lights sorted too...

Kevin Wood

  • Global Moderator
  • *****
  • Offline Offline
  • Gender: Male
  • Alton, Hampshire
  • Posts: 36266
    • Jaguar XE 25t, Westfield
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #6 on: 20 March 2018, 09:44:19 »

Yep, they use cheap components and poor soldering techniques then mount the board where it gets hot. Replace the electrolytics with decent quality 105 C rated parts and check for cracked solder joints on the PCB, particularly on the heavy components like relays and transformers and it'll probably never give any hassle again.
Logged
Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/

STEMO

  • Guest
Re: Viessmann Boiler pcb failure
« Reply #7 on: 20 March 2018, 10:32:02 »

Yep, they use cheap components and poor soldering techniques then mount the board where it gets hot. Replace the electrolytics with decent quality 105 C rated parts and check for cracked solder joints on the PCB, particularly on the heavy components like relays and transformers and it'll probably never give any hassle again.
Told ya  ;D
Logged

Shackeng

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Ramsbury
  • Posts: 7762
    • 3.2 Elite 2.0 TitX Mondeo
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #8 on: 20 March 2018, 11:01:02 »

Shackeng, if you’re intending to keep the boiler long term, maybe worth hanging on to the old pcb, and testing m/repairing it so you have a spare you can drop in in future.

Spooky, 2 mins ago I was looking up firms who repair them! Had it not been this time of year, I would likely have sent it off for repair and done without the boiler for a week or two, but it is still f****ng cold and the new board is due here today, so may send the old one off for overhaul. If only it was like the good old days when you could almost see what was happening on cct boards. Our first colour TV back in 1971 went bang a week or two after I bought it. As it was 160 mile round trip to return it, I had a look and found a burnt connection on a board, soldered a connecting wire, and jobs a good 'un. Very unlikely to  be able to do such with modern micro ccts. :y
Logged

Shackeng

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Ramsbury
  • Posts: 7762
    • 3.2 Elite 2.0 TitX Mondeo
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #9 on: 20 March 2018, 11:01:52 »

Typical, boiler failed to start yesterday AM, on of the coldest days of the year! Unfortunately no fault codes, just no flame indicator. Last fault code from a previous temporary failure a while ago suggested a faulty ignition electrode, so changed that today with no luck. Very helpful guy at Viessmann talked me through the trouble shooting - the manual is 'somewhat tricky' to follow - to deduce it is the pcb, (at £360 and change) >:( However it is 9 years old, and he said that changing both electrodes was sensible at that age anyway. Bloody annoying as it is almost certainly one small twopenny item that's failed on the board, which is impossible for me to test. New board arrives tomorrow on overnight delivery.
Mrs S not pleased at having to rely on fan heaters and a gas fire.

Chances are its a few dried out electrolytics

Quite agree Mark, but beyond my skill to check it. :y
Logged

Shackeng

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Ramsbury
  • Posts: 7762
    • 3.2 Elite 2.0 TitX Mondeo
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #10 on: 20 March 2018, 11:04:34 »

Yep, they use cheap components and poor soldering techniques then mount the board where it gets hot. Replace the electrolytics with decent quality 105 C rated parts and check for cracked solder joints on the PCB, particularly on the heavy components like relays and transformers and it'll probably never give any hassle again.

To be fair to Viessmann, due to the design, these boards don't get very warm, and given the quality of the construction of the rest of the boiler, I guess I'm just unlucky. :y
Logged

Kevin Wood

  • Global Moderator
  • *****
  • Offline Offline
  • Gender: Male
  • Alton, Hampshire
  • Posts: 36266
    • Jaguar XE 25t, Westfield
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #11 on: 20 March 2018, 11:18:06 »

Yep, they use cheap components and poor soldering techniques then mount the board where it gets hot. Replace the electrolytics with decent quality 105 C rated parts and check for cracked solder joints on the PCB, particularly on the heavy components like relays and transformers and it'll probably never give any hassle again.

To be fair to Viessmann, due to the design, these boards don't get very warm, and given the quality of the construction of the rest of the boiler, I guess I'm just unlucky. :y

I was speaking in general based on the boilers I've worked on. If the rest of the boiler is bomb proof, it makes sense to keep a spare board to future proof it. :y
Logged
Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/

Sir Tigger KC

  • Get A Life!!
  • *****
  • Offline Offline
  • Gender: Male
  • West Dorset
  • Posts: 23423
    • 2 Fords
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #12 on: 20 March 2018, 14:07:00 »

Yep, they use cheap components and poor soldering techniques then mount the board where it gets hot. Replace the electrolytics with decent quality 105 C rated parts and check for cracked solder joints on the PCB, particularly on the heavy components like relays and transformers and it'll probably never give any hassle again.

To be fair to Viessmann, due to the design, these boards don't get very warm, and given the quality of the construction of the rest of the boiler, I guess I'm just unlucky. :y

I was speaking in general based on the boilers I've worked on. If the rest of the boiler is bomb proof, it makes sense to keep a spare board to future proof it. :y

Not thinking of a Potterton Profile perchance?  ;D
Logged
RIP Paul 'Luvvie' Lovejoy

Politically homeless ......

Shackeng

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Ramsbury
  • Posts: 7762
    • 3.2 Elite 2.0 TitX Mondeo
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #13 on: 20 March 2018, 17:16:16 »

Collected pcb at midday (delivery slot booked by DPD for 4.30, but I managed to intercept him thanks to helpful DPD Local staff), fitted in 20 mins, we now have heat. :y :y :y :y :y :y
Logged

Kevin Wood

  • Global Moderator
  • *****
  • Offline Offline
  • Gender: Male
  • Alton, Hampshire
  • Posts: 36266
    • Jaguar XE 25t, Westfield
    • View Profile
Re: Viessmann Boiler pcb failure
« Reply #14 on: 20 March 2018, 17:21:50 »

Yep, they use cheap components and poor soldering techniques then mount the board where it gets hot. Replace the electrolytics with decent quality 105 C rated parts and check for cracked solder joints on the PCB, particularly on the heavy components like relays and transformers and it'll probably never give any hassle again.

To be fair to Viessmann, due to the design, these boards don't get very warm, and given the quality of the construction of the rest of the boiler, I guess I'm just unlucky. :y

I was speaking in general based on the boilers I've worked on. If the rest of the boiler is bomb proof, it makes sense to keep a spare board to future proof it. :y

Not thinking of a Potterton Profile perchance?  ;D
Well, now you mention it...  ::) Did you have a PCB you wanted me to repair, BTW?
Logged
Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/