Re: Super Fuse?
« Reply #15 on: 01 June 2020, 08:01:55 »

A 13 amp fuse is just that, to protect a cable up to that rating.

You would be bloody mad to think you could somehow "up-grade cable" and exceed 13 amp loading just because these fuses are rated "Super fuse"!! ::) ::) ::) ::)

One would think so, but on my degree course a large part of one module was taken up with "fuses" !!  In the lab we could consistently get a 13 amp fuse to take up to 25 amps without blowing, especially if the current was increased slowly, pulsed and cooling applied to the "fuse" !!  So called "fast blow" fuses would regularly fail at around 11 amps !

Remember .. a fuse "blowing" is simply the wire overheating and melting ... the quality of the wire, the rate of heat dissapation v the rate of heat application, and even the style, quality and position of the fuse holder all make a big difference to the actual thermodynamics of the item !!

The other thing folks forget is a 13 amp fuse is designed to CARRY 13 amps .. not fail at 13 amps .. it should fail at 13+ a tad .. but they all have "leeway" depending on how well they are made.

If fuses were as good as some folk think they are then electrical items would never catch fire ...  but they do, with regular, and dangerous, monotony

There is no specific rupture rating for a 13A domestic fuse over time, in fact it will potentially carry about 40A for 100 seconds (based on the operating graphs)    :y

What everyone forgets is the fuse is NOT to protect the device, it is to protect the supply.

If the device is pulling current to the point it takes out a fuse, its already got an issue, the fuse clears the fault from the supply (the same is true of circuit breakers etc)  :y

Also, the key cause of fires is loose screws an poor contacts adding resistance to the circuit and getting hot (I2R) whilst pulling far less than the rated operating current
Logged

Lizzie Zoom

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Female
  • South
  • Posts: 7370
    • Omega 3.2 V6 ELITE 2003
    • View Profile
Re: Super Fuse?
« Reply #16 on: 01 June 2020, 19:37:18 »

A 13 amp fuse is just that, to protect a cable up to that rating.

You would be bloody mad to think you could somehow "up-grade cable" and exceed 13 amp loading just because these fuses are rated "Super fuse"!! ::) ::) ::) ::)

One would think so, but on my degree course a large part of one module was taken up with "fuses" !!  In the lab we could consistently get a 13 amp fuse to take up to 25 amps without blowing, especially if the current was increased slowly, pulsed and cooling applied to the "fuse" !!  So called "fast blow" fuses would regularly fail at around 11 amps !

Remember .. a fuse "blowing" is simply the wire overheating and melting ... the quality of the wire, the rate of heat dissapation v the rate of heat application, and even the style, quality and position of the fuse holder all make a big difference to the actual thermodynamics of the item !!

The other thing folks forget is a 13 amp fuse is designed to CARRY 13 amps .. not fail at 13 amps .. it should fail at 13+ a tad .. but they all have "leeway" depending on how well they are made.

If fuses were as good as some folk think they are then electrical items would never catch fire ...  but they do, with regular, and dangerous, monotony

What everyone forgets is the fuse is NOT to protect the device, it is to protect the supply.


I knew as I have already said it is protection for the cable :D ;)
Logged

Matchless

  • Omega Knight
  • *****
  • Offline Offline
  • Gender: Male
  • Nottingham
  • Posts: 1563
    • A white van
    • View Profile
Re: Super Fuse?
« Reply #17 on: 01 June 2020, 20:46:00 »

A 13 amp fuse is just that, to protect a cable up to that rating.

You would be bloody mad to think you could somehow "up-grade cable" and exceed 13 amp loading just because these fuses are rated "Super fuse"!! ::) ::) ::) ::)

One would think so, but on my degree course a large part of one module was taken up with "fuses" !!  In the lab we could consistently get a 13 amp fuse to take up to 25 amps without blowing, especially if the current was increased slowly, pulsed and cooling applied to the "fuse" !!  So called "fast blow" fuses would regularly fail at around 11 amps !

Remember .. a fuse "blowing" is simply the wire overheating and melting ... the quality of the wire, the rate of heat dissapation v the rate of heat application, and even the style, quality and position of the fuse holder all make a big difference to the actual thermodynamics of the item !!

The other thing folks forget is a 13 amp fuse is designed to CARRY 13 amps .. not fail at 13 amps .. it should fail at 13+ a tad .. but they all have "leeway" depending on how well they are made.

If fuses were as good as some folk think they are then electrical items would never catch fire ...  but they do, with regular, and dangerous, monotony

What everyone forgets is the fuse is NOT to protect the device, it is to protect the supply.


I knew as I have already said it is protection for the cable :D ;)

And also the internal earth connections and bond wires of a class 1 electrical product (which relies on an earth connection to protect against electric shock); anything supplied with a BS1363 plug has to be tested at 25A down the earth conductor for a minimum of 100 seconds without catching fire or otherwise becoming dangerous to give the fuse enough time to disconnect the fault.