I want to connect up 3 outside security lights - which will draw a max of 300 watts each. I've got a spare position on my fusebox and a 6amp breaker available.
My question is, can I use 1mm cable to run from the breaker onto the 1st light and then onto 2nd and 3rd
Hopefully I can as I've got the best part of a drum of 1mm cable - fingers crossed.
Thanks - Rob
-
1mm T/E is sufficient depending on cable run. Don`t forget to wire them in parallel
-
1mm T/E is sufficient depending on cable run. Don`t forget to wire them in parallel
Thanks & noted. It's probably about 15m in total ..........
-
1mm T/E is sufficient depending on cable run. Don`t forget to wire them in parallel
Thanks & noted. It's probably about 15m in total ..........
1mm T/E :y
-
Are these cables being run in a conduit rob ?
-
Don't forget it will need signing off
-
Don't forget it will need signing off
Yep
-
Are these cables being run in a conduit rob ?
Wasn't planning on that Steve - the entire run is in a roof ..............
-
Are these cables being run in a conduit rob ?
Wasn't planning on that Steve - the entire run is in a roof ..............
A 20 metre run in an enclosed (less than 100mm) space with a current demand of 4 amps (1000W) at 230V will result in a voltage drop of just under 4V, so 1mm˛ T&E will be fine for your application.
Don't forget to provide a suitable means of isolation.
-
Don't forget it will need signing off
I've got a Biro you can use Rob ;D ;D
-