Water heater choice
« on: 03 March 2015, 18:31:00 »

Hi all.  At the moment in my commercial kitchen the hot water for washing up is supplied by a gas mersey main balanced flue water heater that has just failed. So I am looking for a replacement, either gas or electric. I have seen some under sink 2kw heaters which are a lot cheaper than a gas boiler similar to the one I have at the moment, but I am not sure they would be up to the job. The hot water requirements are about 10 litres every 10 minutes. Any body got any suggestions.

TIA
Tony
Logged
Be aware of mole holes be very aware!

powerslinky

  • Guest
Re: Water heater choice
« Reply #1 on: 03 March 2015, 19:17:15 »

Have a look at a Redring Powerstream Eco  . . .  not sure if it is up to "commercial" use though :'(

But runs a shower & a basin in a bathroom ok   HTH ;)

Edit : around £140  I think  . . . heats the water as you need it  . . . no tank
« Last Edit: 03 March 2015, 19:19:02 by Essex Big Al »
Logged

Bigron

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Witham, Essex
  • Posts: 4808
    • Omega 2.6 V6 Auto '51 Reg
    • View Profile
Re: Water heater choice
« Reply #2 on: 03 March 2015, 19:20:40 »

A quick mental calculation suggests that it might just about make it, assuming that you want the water not much more than hand-hot, i.e. about 50-ish degrees Celcius. Could you fit two, both to have spare capability and in case commercial use is too much for one?

Ron.
Logged

Kevin Wood

  • Global Moderator
  • *****
  • Offline Offline
  • Gender: Male
  • Alton, Hampshire
  • Posts: 36413
    • Jaguar XE 25t, Westfield
    • View Profile
Re: Water heater choice
« Reply #3 on: 03 March 2015, 19:21:30 »

Let's say you want to water heated to 60 degrees C and incoming water is worst case at 5 C.

Water has a heat capacity of 4200j/kgoC and you need 10 litres, which is 10kg.

Heat input needs to be 10 X 4200 X (60-5) = 2.31Mj

A 2kW element gives you 2kj per second. In 10 minutes, that's 2000x60x10 = 1.2 Mj

So no, 2kW is not enough. What's more, you'll need something that stores at least 10 litres of water so you can draw it off in one go, and most under counter ones only have a capacity of a couple of litres.
Logged
Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/

Bigron

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Witham, Essex
  • Posts: 4808
    • Omega 2.6 V6 Auto '51 Reg
    • View Profile
Re: Water heater choice
« Reply #4 on: 03 March 2015, 19:22:13 »

Oops, the italics were meant for just the "might" word in might just about make it!

Ron.
Logged

Taxi_Driver

  • Guest
Re: Water heater choice
« Reply #5 on: 03 March 2015, 19:32:54 »

Let's say you want to water heated to 60 degrees C and incoming water is worst case at 5 C.

Water has a heat capacity of 4200j/kgoC and you need 10 litres, which is 10kg.

Heat input needs to be 10 X 4200 X (60-5) = 2.31Mj

A 2kW element gives you 2kj per second. In 10 minutes, that's 2000x60x10 = 1.2 Mj

So no, 2kW is not enough. What's more, you'll need something that stores at least 10 litres of water so you can draw it off in one go, and most under counter ones only have a capacity of a couple of litres.

I'm certainly not putting my hands in water thats 60C....45C is nearer.....my combi is set to 43C for hot water, and that gives a 'toastie' shower  :y But I suspect a 2kw heater wouldn't be enough....How about an electric shower heater ... 8 or 10 kw that could give that sort temp continuously  :-\
« Last Edit: 03 March 2015, 19:35:42 by Taxi Driver »
Logged

Kevin Wood

  • Global Moderator
  • *****
  • Offline Offline
  • Gender: Male
  • Alton, Hampshire
  • Posts: 36413
    • Jaguar XE 25t, Westfield
    • View Profile
Re: Water heater choice
« Reply #6 on: 03 March 2015, 19:36:42 »

Let's say you want to water heated to 60 degrees C and incoming water is worst case at 5 C.

Water has a heat capacity of 4200j/kgoC and you need 10 litres, which is 10kg.

Heat input needs to be 10 X 4200 X (60-5) = 2.31Mj

A 2kW element gives you 2kj per second. In 10 minutes, that's 2000x60x10 = 1.2 Mj

So no, 2kW is not enough. What's more, you'll need something that stores at least 10 litres of water so you can draw it off in one go, and most under counter ones only have a capacity of a couple of litres.

I'm certainly not putting my hands in water thats 60C....45C is nearer.....my combi is set to 43C for hot water, and that gives a 'toastie' shower  :y But I suspect a 2kw heater wouldn't be enough....3kw?  :-\

Agreed, but HSE (legionella) requirements in commercial premises require it to be at at least 60 degrees C.
Logged
Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/

powerslinky

  • Guest
Re: Water heater choice
« Reply #7 on: 03 March 2015, 19:43:23 »

Let's say you want to water heated to 60 degrees C and incoming water is worst case at 5 C.

Water has a heat capacity of 4200j/kgoC and you need 10 litres, which is 10kg.

Heat input needs to be 10 X 4200 X (60-5) = 2.31Mj

A 2kW element gives you 2kj per second. In 10 minutes, that's 2000x60x10 = 1.2 Mj

So no, 2kW is not enough. What's more, you'll need something that stores at least 10 litres of water so you can draw it off in one go, and most under counter ones only have a capacity of a couple of litres.

I'm certainly not putting my hands in water thats 60C....45C is nearer.....my combi is set to 43C for hot water, and that gives a 'toastie' shower  :y But I suspect a 2kw heater wouldn't be enough....How about an electric shower heater ... 8 or 10 kw that could give that sort temp continuously  :-\

Redring Powerstreams come in 9.5   10.5  or even 12KW   I think  . . .  but don't know if they will do 60 c :-\ :-\
Logged

Taxi_Driver

  • Guest
Re: Water heater choice
« Reply #8 on: 03 March 2015, 19:46:23 »

Let's say you want to water heated to 60 degrees C and incoming water is worst case at 5 C.

Water has a heat capacity of 4200j/kgoC and you need 10 litres, which is 10kg.

Heat input needs to be 10 X 4200 X (60-5) = 2.31Mj

A 2kW element gives you 2kj per second. In 10 minutes, that's 2000x60x10 = 1.2 Mj

So no, 2kW is not enough. What's more, you'll need something that stores at least 10 litres of water so you can draw it off in one go, and most under counter ones only have a capacity of a couple of litres.

I'm certainly not putting my hands in water thats 60C....45C is nearer.....my combi is set to 43C for hot water, and that gives a 'toastie' shower  :y But I suspect a 2kw heater wouldn't be enough....3kw?  :-\

Agreed, but HSE (legionella) requirements in commercial premises require it to be at at least 60 degrees C.

Ah...ok ...now I understand...why my boiler controller has a setting for legionella....its set to off  ::) ;D
Logged

Andy H

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Auckland
  • Posts: 5532
    • Mazda MPV
    • View Profile
Re: Water heater choice
« Reply #9 on: 03 March 2015, 20:09:56 »

Two more points
How much does your gas cost you at the moment? I haven't done a cost comparison recently but electric heating will cost more to run than gas (about 3 times more IIRC)

Also how big is the electricity supply? 12kW on a single phase supply will draw 50 Amps. Even assuming that your distribution board is man enough you may find that you spend most of the cost saving on the electrical supply.
Logged
"Deja Moo - The feeling that you've heard this bull somewhere before."

Tony H

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • liverpool
  • Posts: 4940
  • Black Elites are luurvley
    • View Profile
Re: Water heater choice
« Reply #10 on: 06 March 2015, 21:32:19 »

Hi everyone thanks for the replies especially yours Kevin very thorough  :y you've all  given me plenty of "food for thought" sorry for the pun "I'll get my coat"  ::)