Re: House Electrics
« Reply #15 on: 26 August 2010, 17:36:45 »

Quote
Sounds like the breaker is tripping out due to a fault on the circuit to me.

Yes, me too.

Kevin
Logged
Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/

CaptainZok

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Bolton
  • Posts: 8093
  • Victim of Cyberbullying.
    • 3.2 MV6 Estate
    • View Profile
Re: House Electrics
« Reply #16 on: 26 August 2010, 17:39:24 »

Replace breaker with M6 bolt, switch on and wait for smoke to issue from the installation. Fault found. Seemples. ;D ;D
Logged
PM me for code reading/clearing
TuBy's new whipping boy.

Kevin Wood

  • Global Moderator
  • *****
  • Offline Offline
  • Gender: Male
  • Alton, Hampshire
  • Posts: 36427
    • Jaguar XE 25t, Westfield
    • View Profile
Re: House Electrics
« Reply #17 on: 26 August 2010, 17:41:18 »

Quote
Replace breaker with M6 bolt, switch on and wait for smoke to issue from the installation. Fault found. Seemples. ;D ;D

.. then realise the main switch has welded itself closed and start running around in a panic. ;D

Kevin
Logged
Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/

CaptainZok

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Bolton
  • Posts: 8093
  • Victim of Cyberbullying.
    • 3.2 MV6 Estate
    • View Profile
Re: House Electrics
« Reply #18 on: 26 August 2010, 17:44:00 »

Quote
Quote
Replace breaker with M6 bolt, switch on and wait for smoke to issue from the installation. Fault found. Seemples. ;D ;D

.. then realise the main switch has welded itself closed and start running around in a panic. ;D

Kevin
Insulated wire cutters through the tails then a plastic bucket to catch the electric that runs out always sorts that.
Logged
PM me for code reading/clearing
TuBy's new whipping boy.

Kevin Wood

  • Global Moderator
  • *****
  • Offline Offline
  • Gender: Male
  • Alton, Hampshire
  • Posts: 36427
    • Jaguar XE 25t, Westfield
    • View Profile
Re: House Electrics
« Reply #19 on: 26 August 2010, 19:16:48 »

Quote
Quote
Quote
Replace breaker with M6 bolt, switch on and wait for smoke to issue from the installation. Fault found. Seemples. ;D ;D

.. then realise the main switch has welded itself closed and start running around in a panic. ;D

Kevin
Insulated wire cutters through the tails then a plastic bucket to catch the electric that runs out always sorts that.

You don't need a bucket with leccy. Must be Gas you're thinking about. :y

Kevin
Logged
Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/

pscocoa

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Sandhurst Berkshire
  • Posts: 3761
    • Volvo V90 D5 AWD
    • View Profile
Re: House Electrics
« Reply #20 on: 26 August 2010, 19:56:59 »

there are quite a few recessed ceiling lights and transformers up there to check
Logged
[img name=signat_img_resize]http://[/img]

CaptainZok

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Bolton
  • Posts: 8093
  • Victim of Cyberbullying.
    • 3.2 MV6 Estate
    • View Profile
Re: House Electrics
« Reply #21 on: 26 August 2010, 20:05:17 »

Quote
Quote
Quote
Quote
Replace breaker with M6 bolt, switch on and wait for smoke to issue from the installation. Fault found. Seemples. ;D ;D

.. then realise the main switch has welded itself closed and start running around in a panic. ;D

Kevin
Insulated wire cutters through the tails then a plastic bucket to catch the electric that runs out always sorts that.

You don't need a bucket with leccy. Must be Gas you're thinking about. :y

Kevin
Nah Kev, gas you collect with a bin bag and elastic band everyone knows that.
Logged
PM me for code reading/clearing
TuBy's new whipping boy.

MikeDundee

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Costa Del Peckham
  • Posts: 9370
    • View Profile
Re: House Electrics
« Reply #22 on: 27 August 2010, 06:09:17 »

Quote
House was rewired in 2005. Box is a Wylex NHRS4504 - I can get the mcbs fom Screwfix in Farnborough whch is very local. Cannot get to it today though.

It may well not be the mcb of course but will start with that.

Wylex are a good make, we use them throughout all out installs, rewire in 2005 will be to 16th edition, eletricians now works to 17th edition.

There has been a product recall on faulty MCB's by MCB manufacturer Electrium, so if the MCB is an electrium one, you may need to check with the original installers the product codes to see if it is in the batch that are subject to the product recall :y
Logged

pscocoa

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Sandhurst Berkshire
  • Posts: 3761
    • Volvo V90 D5 AWD
    • View Profile
Re: House Electrics
« Reply #23 on: 27 August 2010, 10:37:41 »

Thanks Mike - the CU is indeed Electrium so will give them a call. Thanks for your input.
Logged
[img name=signat_img_resize]http://[/img]

pscocoa

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Sandhurst Berkshire
  • Posts: 3761
    • Volvo V90 D5 AWD
    • View Profile
Re: House Electrics
« Reply #24 on: 27 August 2010, 10:43:33 »

The only recall is on units fitted between 1st April 2009 and end of Feb 2010. The Wylex MCB in our unti is NSB06 which is referred to in the recall notice but of course ours was a 2005 installation.

Thanks for the idea on this
« Last Edit: 27 August 2010, 10:43:58 by pscocoa »
Logged
[img name=signat_img_resize]http://[/img]

Kevin Wood

  • Global Moderator
  • *****
  • Offline Offline
  • Gender: Male
  • Alton, Hampshire
  • Posts: 36427
    • Jaguar XE 25t, Westfield
    • View Profile
Re: House Electrics
« Reply #25 on: 27 August 2010, 10:44:40 »

A mate of mine did a re-wire earlier in the year and when he powered it up one of the RCBOs went up in smoke. Would have caused a fire if he'd not been standing there watching it, he reckons.  :o Trying to recall what make it was. Could well have been Electrium. I recall that he couldn't get MK ones in the timescale required so went for something less reputable.

Kevin
Logged
Tech2 services currently available. See TheBoy's price list: http://theboy.omegaowners.com/

MikeDundee

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Costa Del Peckham
  • Posts: 9370
    • View Profile
Re: House Electrics
« Reply #26 on: 27 August 2010, 21:12:19 »

Quote
The only recall is on units fitted between 1st April 2009 and end of Feb 2010. The Wylex MCB in our unti is NSB06 which is referred to in the recall notice but of course ours was a 2005 installation.

Thanks for the idea on this

Interesting as electrium MCB's fitted in an 06/07 project are subject to inspectiomn by the installer, being paid by electrium , I have access to the codes if you need them let me know. :y
Logged

Andy H

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Auckland
  • Posts: 5533
    • Mazda MPV
    • View Profile
Re: House Electrics
« Reply #27 on: 27 August 2010, 22:04:52 »

Quote
Quote
Quote
The normal issue is that a bulb has blown and taken the MCB out. I would reset it and see if it trips again.
I assume it's not an RCD or RCBO? In that case, you could have an earth leakage fault that has caused it to trip.

Kevin

We have that problem, every time a bulb blows.. ::) ::)

halogen bulb ?.

They tend to fail by the element breaking off and falling across the terminals, a shorter bit of element, so tries to draw a lot more current and causing an overload. This used to take out normal bulb dimmers quite quickly, as they can't cope with the momentary surge.

Ken
Some of the 'quality' incandescent lamps have a fusible link in the wire between the base and the filament to prevent a failing lamp taking out the circuit.

You can be certain that the cheap or supermarket ones don't. :(
Logged
"Deja Moo - The feeling that you've heard this bull somewhere before."

markspark

  • Senior Member
  • ****
  • Offline Offline
  • Gender: Male
  • Bolton
  • Posts: 600
    • View Profile
Re: House Electrics
« Reply #28 on: 28 August 2010, 16:58:27 »

as said i would first check the mcb remove the live and try resetting the mcb if it does reset mcb should be ok.
you could then take the live out of the downstairs mcb and put the upstairs on that one and switch back on if it then trips the problem if deffo something on the upstairs wireing.
I would them go in loft see if the roof has sprung a leak if not that have a look round for signs of rodent droppings if not that then its time to start splitting the circuit up
if you need advice on doing this drop me a pm
Logged

pscocoa

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Sandhurst Berkshire
  • Posts: 3761
    • Volvo V90 D5 AWD
    • View Profile
Re: House Electrics
« Reply #29 on: 28 August 2010, 18:34:34 »

problem fixed but took ages and a lesson for all i suspect. After a mate checking MCD and eliminating, then checked all switches, ceiling roses, transformers etc etc. Then to loft everything underfloor boards and eliminated the obvious. Then took view as to which ceiling rose was first feed in from consumer unit, disconnected loop, disconnected switch - MCB immediately held, confirmed feed in with meter. Connected loop and it still held. Connected light switch and MCB popped again.

Fitted light switch in another room and it worked. Fitted temporary switch on short wire to ceiling rose and that worked.

Floorboards then up in loft removed wire and drew through new wire and job finished.

Cannot believe that the wire has just shorted for no reason. It was in trunking, had not been disturbed since installation over 5 years ago, no signs of damage. Anyway job done - thanks to all for contributions
Logged