Fitting Electric Shower
« on: 28 May 2009, 20:38:30 »

Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA
Logged
All that is necessary for the triumph of evil is that good men do nothing.

UPVC windows/doors/fascias/soffit/gutters supplied/fitted

Ziad

  • Omega Knight
  • *****
  • Offline Offline
  • Gender: Male
  • Bahrain
  • Posts: 1030
  • They say money talks,but all mine says is Goodbye!
    • View Profile
Re: Fitting Electric Shower
« Reply #1 on: 28 May 2009, 20:46:02 »

I'd suggest you go with the 10 mm wiring. I do not trust these thing on a 6 mm. The wires tend to heat a lot when in use IMO on the 6 mm.  :-/
« Last Edit: 28 May 2009, 20:46:40 by ziad »
Logged

Gareth Lewis

  • Senior Member
  • ****
  • Offline Offline
  • Gender: Male
  • Glossop, Derbyshire
  • Posts: 590
  • eCommerce and Website Design & Implementation
    • View Profile
Re: Fitting Electric Shower
« Reply #2 on: 28 May 2009, 20:52:37 »

Would you like me to ask one of the builders who have been here 9 BLOODY DAYS fitting an electric shower in our house!! >:( >:( >:(

Supposed to be a 5 day job to convert shower room to a wet room type and to get the shower off the combi boiler onto its own power and water supply.

I could have done it quicker myself ;) ;) ;)
Logged
[size=11]Website: www.online-selling.co.uk
Successful Website Solutions
eCommerce and Website Design, Management & Implementation[/b]
[/size]

miggcddave

  • Senior Member
  • ****
  • Offline Offline
  • Gender: Male
  •   south wales
  • Posts: 679
    • View Profile
Re: Fitting Electric Shower
« Reply #3 on: 28 May 2009, 21:11:27 »

Quote
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA
do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill :( :(
Logged

RobG

  • Omega Queen
  • *****
  • Offline Offline
  • Gender: Male
  • Bristol
  • Posts: 13831
  • I might have a link, pic or part number for that
    • 16 plate Mokka. Vivaro
    • View Profile
Re: Fitting Electric Shower
« Reply #4 on: 28 May 2009, 21:16:50 »

Quote
Quote
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA
do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill :( :(
Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. :y
Logged
All that is necessary for the triumph of evil is that good men do nothing.

UPVC windows/doors/fascias/soffit/gutters supplied/fitted

miggcddave

  • Senior Member
  • ****
  • Offline Offline
  • Gender: Male
  •   south wales
  • Posts: 679
    • View Profile
Re: Fitting Electric Shower
« Reply #5 on: 28 May 2009, 21:21:30 »

Quote
Quote
Quote
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA
do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill :( :(
Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. :y
yea that sounds good to me mate but i would use 10mm T/E just to be on the safe side; and if you up grade your shower in the future you got the cable to take it  good luck mate :y
Logged

RobG

  • Omega Queen
  • *****
  • Offline Offline
  • Gender: Male
  • Bristol
  • Posts: 13831
  • I might have a link, pic or part number for that
    • 16 plate Mokka. Vivaro
    • View Profile
Re: Fitting Electric Shower
« Reply #6 on: 28 May 2009, 21:23:45 »

Quote
Quote
Quote
Quote
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA
do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill :( :(
Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. :y
yea that sounds good to me mate but i would use 10mm T/E just to be on the safe side; and if you up grade your shower in the future you got the cable to take it  good luck mate :y
Thought about that. 10mm it`s gonna be (bloody dear though), ah well, what price safety & peace of mind :y
Logged
All that is necessary for the triumph of evil is that good men do nothing.

UPVC windows/doors/fascias/soffit/gutters supplied/fitted

miggcddave

  • Senior Member
  • ****
  • Offline Offline
  • Gender: Male
  •   south wales
  • Posts: 679
    • View Profile
Re: Fitting Electric Shower
« Reply #7 on: 28 May 2009, 21:27:58 »

Quote
Quote
Quote
Quote
Quote
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA
do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill :( :(
Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. :y
yea that sounds good to me mate but i would use 10mm T/E just to be on the safe side; and if you up grade your shower in the future you got the cable to take it  good luck mate :y
Thought about that. 10mm it`s gonna be (bloody dear though), ah well, what price safety & peace of mind :y
have you had a look at screw fix direct good prices in that book ; worth a look its on line  :y
Logged

RobG

  • Omega Queen
  • *****
  • Offline Offline
  • Gender: Male
  • Bristol
  • Posts: 13831
  • I might have a link, pic or part number for that
    • 16 plate Mokka. Vivaro
    • View Profile
Re: Fitting Electric Shower
« Reply #8 on: 28 May 2009, 21:34:22 »

Quote
Quote
Quote
Quote
Quote
Quote
Hi Guys, Fitting an 8.5Kw (cheapo Triton) shower for a mate`s mate. 15 metre pretty much straight run from consumer unit. Is 6mm cable gonna do or will I have to up it to 10mm. TIA
do you now the regs on fitting a shower .rcd switch earth cable thickness shower switch with pull cord earth cable on all pipe work ? if you are not sure mate get a spark to fit it if it goes wrong a shower will kill :( :(
Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. :y
yea that sounds good to me mate but i would use 10mm T/E just to be on the safe side; and if you up grade your shower in the future you got the cable to take it  good luck mate :y
Thought about that. 10mm it`s gonna be (bloody dear though), ah well, what price safety & peace of mind :y
have you had a look at screw fix direct good prices in that book ; worth a look its on line  :y
I`ll have a gander. Usually get most of my stuff from "Toolstation" :)
Logged
All that is necessary for the triumph of evil is that good men do nothing.

UPVC windows/doors/fascias/soffit/gutters supplied/fitted

miggcddave

  • Senior Member
  • ****
  • Offline Offline
  • Gender: Male
  •   south wales
  • Posts: 679
    • View Profile
Re: Fitting Electric Shower
« Reply #9 on: 28 May 2009, 21:46:30 »

25 mtr reel for £48 10mm t/e in screw fix with vat :-/
Logged

RobG

  • Omega Queen
  • *****
  • Offline Offline
  • Gender: Male
  • Bristol
  • Posts: 13831
  • I might have a link, pic or part number for that
    • 16 plate Mokka. Vivaro
    • View Profile
Re: Fitting Electric Shower
« Reply #10 on: 28 May 2009, 21:47:47 »

Quote
25 mtr reel for £48 10mm t/e in screw fix with vat :-/
Same bloody price @ the Toolstation :'( :'(
Logged
All that is necessary for the triumph of evil is that good men do nothing.

UPVC windows/doors/fascias/soffit/gutters supplied/fitted

miggcddave

  • Senior Member
  • ****
  • Offline Offline
  • Gender: Male
  •   south wales
  • Posts: 679
    • View Profile
Re: Fitting Electric Shower
« Reply #11 on: 28 May 2009, 21:50:59 »

Quote
Quote
25 mtr reel for £48 10mm t/e in screw fix with vat :-/
Same bloody price @ the Toolstation :'( :'(
oh well ? but like you siad safety first
Logged

KillerWatt

  • Guest
Re: Fitting Electric Shower
« Reply #12 on: 28 May 2009, 23:10:14 »

Quote
Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. :y
That's double pole isolator with indication, and you need to be Part P for anything concerning a bathroom.

It's more than just cable length versus current drain when carrying out an installation.

Seriously, get a qualified sparks in.....because a mistake can see you in the dock for manslaughter if something tragic occurs.
Logged

crazyjoetavola

  • Guest
Re: Fitting Electric Shower
« Reply #13 on: 28 May 2009, 23:13:13 »

Quote
Quote
Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. :y
That's double pole isolator with indication, and you need to be Part P for anything concerning a bathroom.

It's more than just cable length versus current drain when carrying out an installation.

Seriously, get a qualified sparks in.....because a mistake can see you in the dock for manslaughter if something tragic occurs.


Wise words Killer :y :y
Logged

miggcddave

  • Senior Member
  • ****
  • Offline Offline
  • Gender: Male
  •   south wales
  • Posts: 679
    • View Profile
Re: Fitting Electric Shower
« Reply #14 on: 28 May 2009, 23:13:40 »

Quote
Quote
Yeah, I know all that mate, 45A MCB @ consumer unit, 30ma RCCB protecting the circuit and a 45A double pole isolating pull cord/switch. Just wondering whether the 6mm T/E will de-rate due to the cable run. :y
That's double pole isolator with indication, and you need to be Part P for anything concerning a bathroom.

It's more than just cable length versus current drain when carrying out an installation.

Seriously, get a qualified sparks in.....because a mistake can see you in the dock for manslaughter if something tragic occurs.
well siad K W thats the words i was looking for  :y