Re: Potterton Suprima
« Reply #30 on: 20 December 2010, 13:08:20 »

Quote
Just a bit of info that may save someone time and trouble. If you get the dreaded lock out situation on the Suprima HE check for a frozen condensate pipe outside the house. This will be quite common at these temperatures. Going to get some lagging now it is cleared again. Might save you call out fees even if insured as frozen pipes often not covered by policies

New PCB cleared previous problem (original post) by the way

Which will be as a result of incorrect installation by a monkey with a certificate!

They need to teach these fitters to read as part of the gas safe process!
Logged

pscocoa

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Sandhurst Berkshire
  • Posts: 3761
    • Volvo V90 D5 AWD
    • View Profile
Re: Potterton Suprima
« Reply #31 on: 20 December 2010, 13:12:53 »

Thanks Marks - what is correct instruction on this if you have it please or link to what should have been done? Much appreciated if you have something.
Logged
[img name=signat_img_resize]http://[/img]

Marks DTM Calib

  • Administrator
  • *****
  • Offline Offline
  • Gender: Male
  • West Bridgford
  • Posts: 34016
  • Git!
    • View Profile
Re: Potterton Suprima
« Reply #32 on: 20 December 2010, 13:32:26 »

Potterton have some decent info in the installation manual from memory.

The basics are that if its external it needs to be in 32mm pipe (waste pipe), idealy insulated and have a fall of 50mm in 1m.

Have a look at appendix B of this:

http://www.gov.je/SiteCollectionDocuments/Planning%20and%20building/ID%20AssessmentGuidetoCondensingBoilerInstallationinDwellings%2020100910%20mm.pdf
« Last Edit: 20 December 2010, 13:41:53 by Mark »
Logged

aaronjb

  • Guest
Re: Potterton Suprima
« Reply #33 on: 20 December 2010, 13:36:16 »

I'm glad mine is indoors .. well, in a sort of half-indoor cupboard (gets down to 5.5C in this weather but no lower).. although there is a nice 'uphill' section in the pipe thanks to my plumber who was apparently unfamiliar with the concept of gravity..  :D
Logged

Marks DTM Calib

  • Administrator
  • *****
  • Offline Offline
  • Gender: Male
  • West Bridgford
  • Posts: 34016
  • Git!
    • View Profile
Re: Potterton Suprima
« Reply #34 on: 20 December 2010, 13:39:10 »

Quote
I'm glad mine is indoors .. well, in a sort of half-indoor cupboard (gets down to 5.5C in this weather but no lower).. although there is a nice 'uphill' section in the pipe thanks to my plumber who was apparently unfamiliar with the concept of gravity..  :D

They truely are useless over priced workers arnt they!
Logged

Andy B

  • Get A Life!!
  • *****
  • Online Online
  • Gender: Male
  • Bury Lancs
  • Posts: 39778
    • ML350 TDM SmartRoadster
    • View Profile
Re: Potterton Suprima
« Reply #35 on: 20 December 2010, 13:43:41 »

Quote
I'm glad mine is indoors .. well, in a sort of half-indoor cupboard (gets down to 5.5C in this weather but no lower).. although there is a nice 'uphill' section in the pipe thanks to my plumber who was apparently unfamiliar with the concept of gravity..  :D

My boiler is in what used to my airing cupboard and doesn't have an external wall, so my boiler condensates into a saniflow type tank complete with pump that pumps it up trough my roof into the gutter. This was at my suggestion verses how he wanted to plumb the bottom feed boiler into where the original boiler was sited.
« Last Edit: 20 December 2010, 13:45:07 by Andy_B »
Logged

pscocoa

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Sandhurst Berkshire
  • Posts: 3761
    • Volvo V90 D5 AWD
    • View Profile
Re: Potterton Suprima
« Reply #36 on: 20 December 2010, 13:47:27 »

Quote
Potterton have some decent info in the installation manual from memory.

The basics are that if its external it needs to be in 32mm pipe (waste pipe), idealy insulated and have a fall of 50mm in 1m.

Have a look at appendix B of this:

http://www.gov.je/SiteCollectionDocuments/Planning%20and%20building/ID%20AssessmentGuidetoCondensingBoilerInstallationinDwellings%2020100910%20mm.pdf

Thanks for that - my pipe is 4m external - now reduced to about 1.5m. It was only 25mm in diameter which might have been ok under old regs but certainly is not now.

Apparently even the 32mm has been freezing at other houses.
Logged
[img name=signat_img_resize]http://[/img]

Marks DTM Calib

  • Administrator
  • *****
  • Offline Offline
  • Gender: Male
  • West Bridgford
  • Posts: 34016
  • Git!
    • View Profile
Re: Potterton Suprima
« Reply #37 on: 20 December 2010, 13:49:33 »

Quote
Quote
I'm glad mine is indoors .. well, in a sort of half-indoor cupboard (gets down to 5.5C in this weather but no lower).. although there is a nice 'uphill' section in the pipe thanks to my plumber who was apparently unfamiliar with the concept of gravity..  :D

My boiler is in what used to my airing cupboard and doesn't have an external wall, so my boiler condensates into a saniflow type tank complete with pump that pumps it up trough my roof into the gutter. This was at my suggestion verses how he wanted to plumb the bottom feed boiler into where the original boiler was sited.

Only acceptable if you have a combined foul and surface water drain..
Logged

aaronjb

  • Guest
Re: Potterton Suprima
« Reply #38 on: 20 December 2010, 13:49:49 »

Quote
Quote
I'm glad mine is indoors .. well, in a sort of half-indoor cupboard (gets down to 5.5C in this weather but no lower).. although there is a nice 'uphill' section in the pipe thanks to my plumber who was apparently unfamiliar with the concept of gravity..  :D

They truely are useless over priced workers arnt they!

I can't complain too much - he fitted it in October and still hasn't sent me the bill! (He was my next door neighbour - now moved further south) ... maybe he'll forget ;)


Quote
My boiler is in what used to my airing cupboard and doesn't have an external wall, so my boiler condensates into a saniflow type tank complete with pump that pumps it up trough my roof into the gutter. This was at my suggestion verses how he wanted to plumb the bottom feed boiler into where the original boiler was sited.

Mine is in what is essentially the gas meter/electric meter/fuse box cupboard which has an inspection hatch into the downstairs bathroom (it's a weird sort of half room thing).  It's on an outside wall, so the over-pressure vent is piped outside, but the condensate drain is piped down into the main soil pipe since it's not more than 4' away, which was handy.

Though I was a bit worried that the cupboard might drop below freezing (it's not very well insulated.. the whole house isn't!), fortunately it's lowest temp is above freezing (and just below the frost protection temp on the boiler)..
Logged

Marks DTM Calib

  • Administrator
  • *****
  • Offline Offline
  • Gender: Male
  • West Bridgford
  • Posts: 34016
  • Git!
    • View Profile
Re: Potterton Suprima
« Reply #39 on: 20 December 2010, 13:51:09 »

Quote
Quote
Potterton have some decent info in the installation manual from memory.

The basics are that if its external it needs to be in 32mm pipe (waste pipe), idealy insulated and have a fall of 50mm in 1m.

Have a look at appendix B of this:

http://www.gov.je/SiteCollectionDocuments/Planning%20and%20building/ID%20AssessmentGuidetoCondensingBoilerInstallationinDwellings%2020100910%20mm.pdf

Thanks for that - my pipe is 4m external - now reduced to about 1.5m. It was only 25mm in diameter which might have been ok under old regs but certainly is not now.

Apparently even the 32mm has been freezing at other houses.

The regs state that insulation is required in exposed locations
Logged

CaptainZok

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Bolton
  • Posts: 8093
  • Victim of Cyberbullying.
    • 3.2 MV6 Estate
    • View Profile
Re: Potterton Suprima
« Reply #40 on: 20 December 2010, 13:53:45 »

Quote
Quote
Quote
I'm glad mine is indoors .. well, in a sort of half-indoor cupboard (gets down to 5.5C in this weather but no lower).. although there is a nice 'uphill' section in the pipe thanks to my plumber who was apparently unfamiliar with the concept of gravity..  :D

My boiler is in what used to my airing cupboard and doesn't have an external wall, so my boiler condensates into a saniflow type tank complete with pump that pumps it up trough my roof into the gutter. This was at my suggestion verses how he wanted to plumb the bottom feed boiler into where the original boiler was sited.

Only acceptable if you have a combined foul and surface water drain..
According to a mate's Dad who was a plumber all his life nowhere in the borough has seperate drains, tis but another southern frippery we manage without oop north. ;D
« Last Edit: 20 December 2010, 13:54:09 by CaptainZok »
Logged
PM me for code reading/clearing
TuBy's new whipping boy.

Marks DTM Calib

  • Administrator
  • *****
  • Offline Offline
  • Gender: Male
  • West Bridgford
  • Posts: 34016
  • Git!
    • View Profile
Re: Potterton Suprima
« Reply #41 on: 20 December 2010, 13:55:56 »

Quote
Quote
Quote
Quote
I'm glad mine is indoors .. well, in a sort of half-indoor cupboard (gets down to 5.5C in this weather but no lower).. although there is a nice 'uphill' section in the pipe thanks to my plumber who was apparently unfamiliar with the concept of gravity..  :D

My boiler is in what used to my airing cupboard and doesn't have an external wall, so my boiler condensates into a saniflow type tank complete with pump that pumps it up trough my roof into the gutter. This was at my suggestion verses how he wanted to plumb the bottom feed boiler into where the original boiler was sited.

Only acceptable if you have a combined foul and surface water drain..
According to a mate's Dad who was a plumber all his life nowhere in the borough has seperate drains, tis but another southern frippery we manage without oop north. ;D

Ow dear, another plumber talking out his ass.

Its been a requirement of the regs for 20+ years so all recent build will have them.

Logged

CaptainZok

  • Omega Lord
  • *****
  • Offline Offline
  • Gender: Male
  • Bolton
  • Posts: 8093
  • Victim of Cyberbullying.
    • 3.2 MV6 Estate
    • View Profile
Re: Potterton Suprima
« Reply #42 on: 20 December 2010, 13:57:37 »

Quote
Quote
Quote
Quote
Quote
I'm glad mine is indoors .. well, in a sort of half-indoor cupboard (gets down to 5.5C in this weather but no lower).. although there is a nice 'uphill' section in the pipe thanks to my plumber who was apparently unfamiliar with the concept of gravity..  :D

My boiler is in what used to my airing cupboard and doesn't have an external wall, so my boiler condensates into a saniflow type tank complete with pump that pumps it up trough my roof into the gutter. This was at my suggestion verses how he wanted to plumb the bottom feed boiler into where the original boiler was sited.

Only acceptable if you have a combined foul and surface water drain..
According to a mate's Dad who was a plumber all his life nowhere in the borough has seperate drains, tis but another southern frippery we manage without oop north. ;D

Ow dear, another plumber talking out his ass.

Its been a requirement of the regs for 20+ years so all recent build will have them.

As he's been dead for most of the last 20 years I'd imagine he was spot on at the time.
Logged
PM me for code reading/clearing
TuBy's new whipping boy.

pscocoa

  • Omega Baron
  • *****
  • Offline Offline
  • Gender: Male
  • Sandhurst Berkshire
  • Posts: 3761
    • Volvo V90 D5 AWD
    • View Profile
Re: Potterton Suprima
« Reply #43 on: 20 December 2010, 14:14:07 »

we have separate foul and rainwater drains - can condensate go to either then?
Logged
[img name=signat_img_resize]http://[/img]

Marks DTM Calib

  • Administrator
  • *****
  • Offline Offline
  • Gender: Male
  • West Bridgford
  • Posts: 34016
  • Git!
    • View Profile
Re: Potterton Suprima
« Reply #44 on: 20 December 2010, 14:22:18 »

Quote
we have separate foul and rainwater drains - can condensate go to either then?

No, its slightly acid so can NOT go into the surface water drains
Logged